Answer to the assignment question.
Title
Question
Madam/sir,
In the assignment you have given I have solved it in two ways one is with manual reset and second one is with automatic reset. After thinking for long I developed that program. Please check that also.
https://drive.google.com/file/d/1rEcqj1ZtoKvty0ESMOl5uMseN8kRGkpy/view?usp=sharing
https://drive.google.com/file/d/1WPJtREMOB2xu1QzTCQgNWcCTVv0-_uZZ/view?usp=sharing

The above two are complied and saved file of first program.


The following two are the second program's compiled and saved files:-
https://drive.google.com/file/d/1PMKpRjvtuzLFw2gaSuDGP7zHvPu-t6JB/view?usp=sharing
https://drive.google.com/file/d/1BWstrk03Mt1F83bwKujwDqyIW5qf48cE/view?usp=sharing

Please reply me for the answer, for both the types .

OpenPLC-with-LDmicro CTU-Counter 09-10 min 50-60 sec 10-06-22, 9:41 p.m. sc256356

Answers:

The logic of both the files you have shared are correct.

But the question we have asked in the tutorial is to reset the counter using another Contact (which you have done in CTUMADAMSTUTORIAL.ld).

In the logic CTU.ld you are basically implementing a circular counter using CTU.
15-06-22, 4:03 p.m. NirmalaVenkat